We need to know more information about your site before recommending HDPE.
Normally you would want to use PVC pipe for sewer. It's resistant to hydrogen sulfide gas from the sewer flow. PVC is fairly tough and stiff so it can be installed easily on the grade/design slope.
HDPE is tougher than PVC. It's also not as stiff, it bends easily, therefore installing without creating low spots is a problem. And HDPE has to fused together to joint two pipes. Fusing takes about 20 minutes per joint and is typically done to the entire pipeline next to the trench. So you need a lot of area for the fused pipe storage.
In a normal situation I wouldn't use HDPE pipe for sewer. I used HDPE for sewer once, it is the first horizontal directional drilled HDPE gravity sewer line installed in Arizona.
But your site specific issues may require HDPE.
------------------------------