EPA literature regarding revisions to the total coliform rule. Excerpt below
Utilities commonly have a significant amount of leakage throughout the distribution system. In a
survey conducted by Kirmeyer et al. (2001), 18 of 26 utilities surveyed had sufficient metering
data to determine loss through leaks and breaks in terms of a percentage of total water produced.
Seventeen utilities reported that less than 10% of total water produced is lost to leaks and breaks.
One utility reported that water loss due to leaks and breaks is 18% of total water produced.
Leakage points that are submerged may provide opportunities for intrusion of contaminated
water during transient pressure events (Kirmeyer, et. al., 2001). Pressure changes in the
distribution system can result in hydraulic surges that create low or negative pressure waves,
which often go undetected by water system operators. As a low or negative pressure wave
passes through a pipe, it can cause untreated, exogenous water to be drawn into the pipe through
points of leakage or cross-connections. Sources of these pressure changes can be the effects of
routine distribution system operation, such as pump startup and shutdown, opening and closing
fire hydrants, and sudden changes in water demand (Kirmeyer et al., 2001). Further detail
regarding the introduction of contaminants through intrusion is provided in the Distribution
System White Paper The Potential for Health Risks from Intrusion of Contaminants into the
Distribution System from Pressure Transients (LeChevallier et al., 2002).
------------------------------
Justin Mahon P.E., M.ASCE
SENIOR ENGINEER
Oradell NJ
(201) 967-8177
------------------------------
Original Message:
Sent: 12-07-2018 14:09
From: Barbara Whitten
Subject: Pathogens in the Water Supply
Here is a question that was sent to EWRI staff. Can anybody provide any insight into this situation?:
"Can someone explain or lead me to a source of scientific information that can explain why low water pressure allows pathogens to enter the supply piping as opposed to normal pressure, making it necessary to issue a boil water advisory?"
------------------------------
Barbara Whitten A.M.ASCE
Technical Manager
EWRI
------------------------------