Hi,
I am facing a challenge in the current project i am working on. We are designing the Pedestal and the Anchor bolt for the Steel Column to Pedestal Connection and we are using Anchor rods with tack welded Heavy Hex Nut at the bottom with washer Plate. Since the forces are quite Huge we have used Anchor Reinforcement for the Tension and Shear Breakouts. The problem we are facing is with regards to "Pry Out" failure under shear loads. We are not able to satisfy the Pry Out Capacity.
Now reading a little literature and the code commentary i understand that PRY OUT failure mainly happens for Short and Stiff anchors around 4 to 6 times diameter. The code treats the failure as a pseudo Tension failure and uses the same capacity as that of tension cone break out, since the failure cone for pry out and tension breakout are both very similar and start from the head of the anchor bolt.
The anchor bolts that we typically use have a minimum 12d embedment and mostly much more than this to provide sufficient development length to rebar above and below the failure plane. My Question is :
1.) Is the same clause applicable for such long anchors, since pryout seams improbable in such a circumstance. Should we rally check Pry out for anchor bolts around 12 times diameter.
2.) Since the capacity for the Pry out is a step function based on the Tension cone breakout capacity varying from 1 times to 2 times the Breakout capacity, can we use the capacity of Anchor reinforcement instead of concrete, since the same reinforcement which prevents the tension cone breakout will also tie the pry out failure crack.
Will really appreciate your feedback.
Thanks
------------------------------
Mandeep Singh Kohli CP, M.ASCE
Senior Engineer
India
------------------------------