Mr. Chien: I assume you are with a regulatory organization. Let go back to the beginning. All of the comments are spot on, but somewhat incomplete. I would not install a water line unless there was sufficient knowledge about the soils. I have seen soils so hot that the plastic wrap looked like it was used for shotgun practice. Even sandy soil can have enough clay to create electrolysis. So consult a cathodic expert. I have seen soils that will cause DI leakage in less than 10 years.
Crossing close to a gas line, probably protected with induced current, could cause corrosion in the metallic water line and there are other factors. If the water line has sacrificial anodes, are they installed correctly and spaced properly, and are the pipeline jumper connections (which carry current across gasketed joints to the anodes) welded sufficiently, and are there two jumpers in case one fails. Consider anodes on the pipe section that is crossing the gas line and install it so it is approximately in the middle of the waterline pipe section.
Gas companies have been using the best cathodic technology for years. Their systems are strong and exists to protect the gas line, not the surrounding utilities. I have not seen where a water jet from a waterline pin hole punctured a gas line, but it sounds like a lot of liability for the water line owner. A lot of national standards addressing protection from electrolysis are available, but I am retired and have not kept current files, but they are worth looking at.
------------------------------
Bruce Yates P.E., M.ASCE
------------------------------
Original Message:
Sent: 12-27-2019 11:47
From: Tsungchu Chien
Subject: Vertical separation distance between gas line and potable water main
Hi there,
When a proposed water main is crossing perpendicular to an existing gas line, is there any requirement (in California) of the vertical separation distance?
The proposed water main is a 12" ductile pipe, pressure class is 350 psi, operating pressure is 75 psi.
The existing gas line is 2" natural gas line.
Is 4" to 6" or vertical separation sufficient?
Thank you for your thoughts.
------------------------------
Tsungchu Chien P.E., M.ASCE
State Water Resources Control Board
------------------------------