Once you have determined the peak flow rate into the sump the minimum design volume necessary would be:
V(min) = Q(out)*T(min)/4
Q(out) = the pumping rate which is assumed to be half of the peak inflow rate.
T(min) = Minimum cycle time between pump starts.
If the pump rate is NOT half of the peak inflow rate then you would need to write the formula in terms of T(min) and solve by an iterative process:
T(min) = [V(min)/Q(in)] + [V(min)/Q(out)-Q(in))]
------------------------------
Daniel Rosenberg P.E., M.ASCE
AECOM
Cleveland OH
(216)416-2000
------------------------------
Original Message:
Sent: 12-25-2018 08:20
From: Michael Meadows
Subject: Sump Pump Design
My experience is that you would design for average daily flow (ADF) multiplied by a peaking factor that is set by local regulations. I expect peaking factor values vary. What values have others in your location used?
------------------------------
Michael Meadows Ph.D., P.E., F.ASCE
Assoc Professor
Univ Of South Carolina
Columbia SC
(803) 777-3614
Original Message:
Sent: 12-24-2018 04:21
From: Syed Alvi
Subject: Sump Pump Design
Hello everyone,
I want to design a sump pump for a sewage system. For designing this sump volume an influent (incoming) discharge is required. I just need to know is we take peak discharge or average discharge for designing the volume of sump?