The issue with replacing a water main, with a new water main at the same elevation is when you need to make connections to perpendicular mains.
1) In the future when the Utility needs to tap the new water main they now have to cut through the old main.
2) We require the old main to stay in service until the new main has been tested and approved for use. They make all perpendicular connections while the existing main is live. This isn't possible if the new main is still live.
I can understand the same elevation when it is just a large diameter transmission main, but for small diameter mains (12-inch and under) there is no reason not to install the water main at a different elevation.
------------------------------
James Konigsfeld P.E., M.ASCE
Principal Engineer
Seattle WA
------------------------------
Original Message:
Sent: 04-05-2019 07:38
From: Joshua Chabot
Subject: Omitting Profiles from Waterline Construction Plans?
​We recently began working with the city of Quincy, MA and pushed out a package exactly as you are describing, water main replacement and improvements of approximately 11,000LF with plan view only. The city has done these types of packages in the past and expressed no concerns not having profiles, the main difference is all of the proposed pipe is intended to be replaced at the same line and grade of the old pipe, which theoretically will take care of any utility crossings and in the case of this city, minimize the amount of rock excavation. Past projects of new pipe in new trench in dense urban settings we have always shown profiles.
You can see several of the city's previous packages on their purchasing site, Quincy, MA - Current Bids
Quincyma |
remove preview |
|
Quincy, MA - Current Bids |
Please note: We have added a new feature; "CONTRACT AWARD" It is only the front page of the contract, but contains the amount and the terms. If you need a copy of the complete contract, please put in a FOIA request to <maskemail>purchasing@...</maskemail> |
View this on Quincyma > |
|
|
------------------------------
Joshua Chabot P.E.
Tetra Tech
Marlborough MA
Original Message:
Sent: 04-04-2019 21:07
From: Will Bulloss
Subject: Omitting Profiles from Waterline Construction Plans?
My organization is contemplating if/when it is appropriate to show profiles versus plan-only on water main construction plans. Our projects are predominately urban in nature (alignment within roadway with numerous utility crossings), are 3,000-5,000 linear feet in length, and are both distribution system extension or replacement in nature. Pipe diameters are generally 8" and 12". We also have rural projects that are generally extensions along the shoulder of roadways.
I am wondering if others have a decision framework to support the concept of omitting profiling water lines in similar circumstances. The argument is that omitting profiles on relatively smaller and less complex projects allows for more rapid plan development and construction.
I would appreciate any insight you all may have.
------------------------------
Will Bulloss
Blacksburg VA
(540) 207-2323
------------------------------