There may be a better place to post this comment/QA but I had some difficulty finding an appropriate channel to start the discussion.
ASCE 7-22 (and ASCE 7-16) Chapter 30 - Components and Cladding - Section 30.9, addresses the wind forces on building canopies. According to Figure 30.9-1B, the maximum net uplift pressure coefficient for a single-surfaced cladding component (say a connection from purlin to a WF beam) that supports 100 ft^2 of roof area, where hc/he is < 0.5, is slightly less than -0.5 (in magnitude). This seems quite low but for wind into the face of the wall it make sense that positive pressures above and below the canopy surface could develop when hc/he is small, but with some differential. When wind is parallel with the wall, it seems like it could be quite different.
In contrast, a free-standing, mono-sloped flat roof (Section 30.5, Figure 30.5-1), has variable net pressure coefficient for design of cladding components, ranging from -1.1 to -1.2 for clear and obstructed wind flow. At edges and corners of a fee-standing roof, the coefficients can be much greater.
In a situation where a building canopy is disproportionally large, (e.g., extends 80-ft out from the face of the building, and they do exist) and particularly when the wind direction is parallel to the side of the building wall that the canopy is attached to, couldn't the canopy (further from the building) possibly be subjected to pressures more like that of a free-standing roof? I think the provisions of 30.9, as they have been written and without constraints on their use, opens the door for designing cladding for very large canopies for forces much lower than they might experience in design wind event. Section 30.9 also makes no distinction between wind parallel to and normal to the wall the canopy is attached to. I assume the figures are meant to envelope the demands for both directions?
Has there been any discussion about adding some restrictions on the application of 30.9? For example, limiting the application to canopies roofs of a particular maximum dimension, beyond which some other provision (such as 30.5) would take over?
------------------------------
David Webster Ph.D., P.E., S.E., M.ASCE
Senior Structural Engineer
Seattle WA
------------------------------