What is a typical allowance for live loads on residential floors?

  • 1.  What is a typical allowance for live loads on residential floors?

    Posted 01-31-2019 12:35 PM
    Edited by Tirza Austin 01-31-2019 12:34 PM
    A friend has multiple fishtanks in a room on the second floor of his home, a residence built during the 1950's (wood floor over joists) in the Washington, D.C. suburbs. I can calculate the additional live load (psi) that these aquariums impose over the floor system but I need a quick reference to check this load against the typical live load allowances for this type of house. I appreciate advice on what live load values/references we could use to assess the safety of this situation because I have not worked on residential floor systems for years. Thanks!

    ------------------------------
    Rodolfo Pérez P.E., M.ASCE
    Independent Consultant
    Silver Spring MD
    (301) 5024024
    ------------------------------


  • 2.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-01-2019 07:43 AM
    Edited by Tirza Austin 02-01-2019 07:42 AM
    For existing buildings where limited or no information is available we have used 'reverse' engineering approach i.e. to take inventory of existing structure, assess its condition and estimate residual load carrying capacity.

    Then modify/strengthen the structure as dictated by additional load requirements. 

    Regards, 

    ------------------------------
    Shashank Pendharkar Aff.M.ASCE
    Pendharkar & Associates Ltd
    Dar Es Salaam
    255754461650
    ------------------------------



  • 3.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-01-2019 07:43 AM
    The current code in most jurisdictions is 30 PSF for Sleeping Rooms and 40 PSF for other areas. In the 1950's I doubt that much thought went into the floor live loads, and the joists may be undersized. Do you have any additional information about the actual size, span, and spacing of the joists?

    ------------------------------
    Andrew Holmes P.E., L.S., M.ASCE
    Consulting Engineer
    Melbourne FL
    (859)3969628
    ------------------------------



  • 4.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-02-2019 11:44 PM
    Edited by Tirza Austin 02-02-2019 11:43 PM
    I want to thank the nine colleagues for their thoughtful attention to my question on the subject topic. Your collective insights provide me with credible reference and logic to answer the question. Much obliged!


    ------------------------------
    Rodolfo Perez P.E., M.ASCE
    Independent Consultant
    Rodolfo E. Perez, PE, Consulting Engineer
    Silver Spring MD
    (301) 942-8612
    ------------------------------



  • 5.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-01-2019 07:44 AM
    Edited by Tirza Austin 02-01-2019 07:43 AM
    Per ASCE 7-10, bedrooms must be designed for at least 30psf and all other floors must be designed for at least 40psf. The descriptions in the table in ASCE 7-10 chapter 4 - Live Loads are more detailed than this, but that's the gist of it.

    ------------------------------
    Paul Chabot P.E., M.ASCE
    Structural & Forensic Engineer
    Metro Detroit Area MI
    (313)717-2137
    ------------------------------



  • 6.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-01-2019 07:45 AM
    Edited by Tirza Austin 02-01-2019 07:44 AM
    Hello Rodolfo,

    You will need to check table R301.5 of the IRC Live load, this is the current code to give you a baseline. IRC is available online for free, see link below:

    https://codes.iccsafe.org/content/IRC2018/chapter-3-building-planning

    I hope this helps point you in the right direction.

    ------------------------------
    Firas Abdelahad P.E., M.ASCE
    Director of Engineering
    Pittsburgh PA
    (561)512-1749
    ------------------------------



  • 7.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-01-2019 09:52 AM
    Edited by Tirza Austin 02-01-2019 09:52 AM
    Normal floor allowable live load is 40 pounds per square foot (psf).  The fish tanks would be considered a live load.  I would calculate the weight of one fish tank in psf and then apply that load to one floor joist with the fish tank live load distributed on the floor joist over the width of the tank to get pounds per lineal foot (plf). I would then apply this lineal load to the floor joist without any other live load.  You would then have a fish tank live load moment on the floor joist.  This fish tank live load could be equated to a uniform distributed load by letting the fish tank moment be equal to w*l^2/8.  Solve for "w" to get a uniform lineal load.  Divide the "w" by the joist spacing and you will have the uniform live load being used by the fish tanks.  Subtract the uniform fish tank live load from 40 to get the remaining live load capacity of the floor joists.  If the uniform fish tank live load is not very much less than the 40 psf live load, then the floor joists are OK.  If the uniform fish tank live load requires 25% of the joist live load capacity, then you inform the owner to restrict the number of people able to be in the room or the amount of heavy furniture placed in the room.

    ------------------------------
    Dennis Young P.E., M.ASCE
    Owner/principle
    Young Engineering, LLC
    Omaha NE
    (402)983-1154
    ------------------------------



  • 8.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-01-2019 10:05 AM
    Edited by Tirza Austin 02-01-2019 10:05 AM
    As others have stated, 30psf was the typical code requirements for second floors.  That would equate to about 6" of water uniformly spread on the floor.

    You can check load and span tables for a quick sanity check to see if their floor joists have a higher capacity​:
    https://www.nelma.org/wp-content/uploads/SPFs-Span-Tables.pdf
    https://www.southernpine.com/span-tables/

    That said, if the tanks are near one end of the joists, it's not as bad as if they were in the middle of the span.  Your main concern would be the shear capacity at the end  of the joist.  You can compare the shear and moment diagrams of a uniformly loaded joist to your actual loading for a quick but inexact comparison (the load tables may be limited by bending but actually have a higher shear capacity; they may be limited by deflection, but actually have a higher shear capacity)

    You'd also need to think about whether the joists bear on a load-bearing wall below, or if they are on a header beam - say over the opening between the living room and dining room below.  In the latter case, you'd also have to check the header.

    That should hopefully get you started.




    ------------------------------
    Greg Thein, PE
    Cleveland, OH
    ------------------------------



  • 9.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-01-2019 01:17 PM
    Edited by Tirza Austin 02-01-2019 01:17 PM
    Currently the live load for residential construction is 40 pound live load, bedrooms is 30 pounds. ​

    ------------------------------
    Eliot Senor P.E., M.ASCE
    President
    Gabriel E Senor, PC
    Hartsdale NY
    (914) 422-0070
    ------------------------------



  • 10.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-01-2019 01:18 PM
    Edited by Tirza Austin 02-01-2019 01:17 PM
    If you know the floor joist size, spacing, and span you can look up the uniform load safely supported in available wood joist tables​.

    To increase capacity if necessary (assuming end support conditions and foundations allow it) you can "sister" the joists (nail a second joist onto each existing - not usually an easy proposition) or add steel angles (say 2x2x1/4) screwed to the bottom of the joists (this takes a bit of engineering to solve: assume tension in the steel and compression in the wood -- maybe also increase bridging?)

    My dad had two fish tanks about 3 ft x 18" x 18" in a Craftsman house built in the twenties -- no problems at all for thirty years.

    Good luck

    ------------------------------
    David Hancock A.M.ASCE
    Principal
    CBT Childs Bertman Tseckares
    Boston MA
    (617) 262-4354
    ------------------------------



  • 11.  RE: What is a typical allowance for live loads on residential floors?
    Best Answer

    Posted 02-01-2019 01:23 PM
    Edited by Rodolfo Perez 03-09-2019 04:27 AM
    Several previous responses have correctly identified the 30 psf Live Load for sleeping rooms above the main entry level, but the question is more complicated because the fish tanks do not qualify as live load. This "water" loading is not transient, but rather continuously applied for a long duration of time, more like a dead load. (This same discussion applies more frequently to water beds in an upstairs bedroom).  Wood as a structural material handles short-term loads much more efficiently than sustained loading, and experiences significant creep over time as it permanently yields away from continuously applied loads.  This characteristic is accounted for in the National Design Specification For Wood Construction (NDS) which adjusts the allowable bending strength downward by a Load Duration Factor Cd=0.9 for load combinations including only dead loads, as opposed to 1.0 for live load combinations.  In other words, a live load allowance of 30 psf is equivalent to a continuously applied "water" load of .9 x 30 = 27 psf.  And if the water loading does not fully displace ALL the live load (as in the case of a waterbed that may or may not have people in it) you still need to allow for that loading as well.   In my experience, most of the turn of the century row homes in Baltimore and Washington do not meet the required 30 psf second floor loading, often calculating in at around 15 - 22 psf.  But on the plus side, your friend's fish tanks are likely against the walls, and (hopefully) near the bearing ends of the floor framing where the bending stresses will be minimal, rather than out in the middle of the span like most waterbeds.

    ------------------------------
    Peter Mc Conaughy P.E., M.ASCE
    Structural Engineer
    MCCON ENGINEERING INC
    KINGSVILLE MD
    (410)5939535
    ------------------------------



  • 12.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-03-2019 04:06 PM
    Edited by Tirza Austin 02-03-2019 04:06 PM
    You might want to also consider that the IRC floor loads do not include direct consideration of long-term creep.   In my experience, with older wood-framed floor systems, heavy loads such as tanks will cause noticeable deflection over time.   Therefore the flooring under the tanks probably should be reinforced.

    ------------------------------
    Gary Osborne M.ASCE
    Principal Engineer
    Foundation Doctor, Inc.
    Highland Village TX
    (972) 318-8800
    ------------------------------



  • 13.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-03-2019 10:33 PM
    Edited by Tirza Austin 02-03-2019 10:33 PM
    There is a lot of good information already provided by other contributors. My added information has to do with the common occurrence of "increased loads" in private residences and apartments that I have witnessed. These increased loads are due to storing books and equipment in living rooms and bedrooms. Sometimes, what I see in actual residences look more like a Library (Reading room LL=60 psf) or storage facility (Light LL=125 psf).

    My general sense is that the older 30 psf and 40 psf code-prescribed loads should probably be increased by designers, architects, and engineers to take into account the likelihood of such increased loads which may happen sometime in the next few decades, long after the designer is no longer in the picture.

    As for fish tanks, one never really knows when and where such tanks will be positioned, short term or long term (creep effects, etc.). So, here's one more uncertainty that may lead us to increase the design live load.

    ------------------------------
    Franz Rad Ph.D., P.E., F.ASCE
    Portland State Univ
    Portland OR
    (503) 725-4205
    ------------------------------



  • 14.  RE: What is a typical allowance for live loads on residential floors?

    Posted 02-05-2019 02:57 PM
    Edited by Tirza Austin 02-05-2019 02:56 PM
    ​A good resource "Residential Building Loads review and roadmap for future progress"  published by ASCE in 2006.  This 50 page book is good background reading for the different loads and references.

    ------------------------------