Discussion: View Thread

  • 1.  REDUCTION FACTOR Ri FOR INTERNAL PRESSURE

    Posted 03-19-2023 08:18 PM
    I have a confusion/doubt over the Reduction factor Ri equation shown in  ASCE7-05 vs ASCE7-10.
     
    ASCE7-05  the equation 6-16 shows as 22,800Aog  there is comma between 22 and 8 however the same in ASCE7-10 equation 26.11-1 there is dot between 22 and 8.
     
    I was designing the building with large unpartioned volumne , building under design unpartioned volume is Vi =233279633 ft3 and Aog = 281525 ft2. 
     
     
    when i apply ASCE7-05 I am mererly getting any reduction in the internal pressure , however same if i apply with ASCE7-10  I am having reduction as 0.32  from 0.55. 


    ------------------------------
    Mohammed Awez Aff.M.ASCE
    Design Engineer
    DUBAI
    ------------------------------


  • 2.  RE: REDUCTION FACTOR Ri FOR INTERNAL PRESSURE

    Posted 03-20-2023 10:54 AM

    Mohammed,

    The denominator in the square root of the Reduction Factor equation for Large Volume Building is twenty-two thousand eight hundred (22,800) ft * Aog (sf), as is shown on ASCE 7-05 equation 6-16. 

    Please try to use the third printing of ASCE 7-10, which incorporates errata identified through March 15, 2013. In this third printing of the standard, the equation for Reduction factor for Large Volume Buildings (Eq. 26.11-1), matches the one shown on ASCE 7-05 (6-16).



    ------------------------------
    Gustavo Escorcia Ing., P.E., M.ASCE
    Structural Engineer
    STV / Ralph Whitehead and Associates
    North Chesterfield VA
    ------------------------------



  • 3.  RE: REDUCTION FACTOR Ri FOR INTERNAL PRESSURE

    Posted 03-20-2023 11:24 AM

    Thanks Gustavo Noted ! 

    Infact 2016 and 2022 have shown 22800

    However I am having merely no reduction if apply the values as per 22800 even my unpartioned volume quite huge? Will this equation ever gives a reduction ?



    ------------------------------
    Mohammed Awez Aff.M.ASCE
    Design Engineer
    DUBAI
    ------------------------------



  • 4.  RE: REDUCTION FACTOR Ri FOR INTERNAL PRESSURE

    Posted 03-20-2023 03:33 PM

    Please note, the reduction factor, Ri, is intended to correct the Internal Pressure Coefficient, GCpi, as a function of Total Area of openings, Aog, and unpartitioned internal volume, Vi, for partially enclosure buildings.

    If you evaluate the

    Lim Ri(Vi, Aog), when Aog → ꝏ, then Ri 1.0

    Lim Ri(Vi, Aog), when Aog 0, then Ri 0.5

    Thus, for very large area of openings, Ri will be closer to 1.0

    And for very reduced area of openings, Ri will be closer to 0.5

    You probably need to verify the deduction of your Vi, Aog, and the enclosure classification of your building.



    ------------------------------
    Gustavo Escorcia Ing., P.E., M.ASCE
    Structural Engineer
    STV / Ralph Whitehead and Associates
    North Chesterfield VA
    ------------------------------