Here is a more clear explanation of what I said.
If I require there is no uplift load to occur below the structure. I would consider both equations
Given W is the ultimate wind load ( what use to be considered 1.6 x te 50 year wind load.)
I would take the more conservative of the two, 1.0 W which would have given me a factor of safety of 1.6 in the past
If considering the compressive bearing pressure under the ballast when checking the soil I would use D +0.6 W = 40 % of the wind uplift or D if W was zero.
As I mention previously was what is missing the resistance factor for the ballast
Original Message:
Sent: 01-23-2024 10:21 PM
From: Christian Parker
Subject: Factor of Safety for Net Uplift Tension in Buildings
I think in the instance of ballasted solar arrays, using D+0.6W vs. 0.6D+0.6W makes a significant difference, since the design output is the required amount of dead load rather than member strength. You'll specify 40% less ballast if you design for 0.6D+0.6W.
I certainly see your point on geotech. Only once have I seen a geotech report in LRFD, and it was clear that they had converted at the end, like we do for US Federal projects "in Metric" (i.e. design it in Imperial, then change the dimensions on deliverables). I get frustrated with Geotechnical Engineers sometimes for putting the burden of managing separate load combinations on structural engineers, but I don't think LRFD promises as much to geotech. When most of the engineering centers around gravity loads it must seem trivial to focus on anything besides "how much weight?" In structures, the greatest technical challenges are in lateral, so it's more obvious to update environmental hazards to a more consistent basis, and bring the gravity loads along for the ride. Not speaking with any authority here of course.
One item I found interesting in the ballasted solar panels issue is that they state specifically that the 0.6 factor is not to account for variability in resisting weight. Apparently, engineers have been mistakenly using 1.0D on the reasoning that they are 100% certain how much the ballast will weigh since they are specifying it. The SEAOC statement clarifies that the 0.6D is intended to reduce the frequency of wind events that could rip everything off the roof, because the ASD 0.6W load is too low to design right at failure.
P.S. stay warm up there! I was tracking the insane temperatures in Calgary all last week. Beautiful city, though.
------------------------------
Christian Parker P.E., M.ASCE
Structural Project Engineer
Chicago IL
Original Message:
Sent: 01-21-2024 06:34 PM
From: David Thompson
Subject: Factor of Safety for Net Uplift Tension in Buildings
The difference between ASD and LFRD has been an on going debate since LRFD has first been introduced. This became quite apparent. when LRFD was introduced to geotechnical engineers. The geotechnical engineer had great difficulty coping with the load combinations. The LRFD combinations provide an envelop of reactions ie 1.2D + W or .9D + W based on the statistical variations of self-weight of permanent loads.
Using D +.6W or .6 D + .6 W give you similar results in ASD
When you referred to ballasted loads using the .D +.6W only accounts for the load affects you then also need to account the variation of the resistance and I believe that is what the SEAOC is referring to as missing.
------------------------------
David Thompson P.E., M.ASCE
Principal
KTA Structural Engineers Ltd.
Calgary AB
Original Message:
Sent: 01-31-2023 09:29 AM
From: Christian Parker
Subject: Factor of Safety for Net Uplift Tension in Buildings
In foundations, we design for overturning by balancing the acting moment and the resisting moment to a minimum factor of safety. However, there are also cases in superstructure where we rely on bearing to transfer force and need to prevent net tension, using structural weight as ballast. I'm working on an existing building with slab on metal deck over bar joists for the roof, where the original designer balanced out uplift forces by providing just enough dead load at ~0.6D to counteract the ASD wind. Overturning from wind acting on the side of some new RTU's creates a small net uplift; my task was to check whether it would unzip the whole bay, assuming a bearing-only connection to the joists. As it turns out, the roof could maintain net downwards force on the joists at ASD wind (0.6D+0.6W), but it failed at LRFD 0.9D+1.0W. I was surprised to realize that the ASD uplift combination is less conservative on dead load resisting uplift (0.6:0.6 = 1:1 vs. 1:0.9). Strange.
When the net uplift is caused by dead load and resisted by dead load, it gets even stranger. It's not uncommon to have long cantilevers (three or four times the backspan) in contemporary construction, resulting in permanent uplift on the back column, under dead load alone. The back column may be stabilized by the dead load within its trib area: dead load against dead load. It got me wondering about design for uplift when dead load is both the bad guy and the good guy.
Say we model the above frame in analysis software with auto combinations--dangerous, I know. The software would create a demand envelope considering many combinations, using 1.2D for downward effects and 0.9D for uplift. If the wind and snow loads are very small by comparison (let's say it's a decorative canopy inside a shopping mall that experiences virtually no environmental hazards), there is a scenario where the dead load could be almost perfectly balanced; say 10 kips uplift due to dead load on the cantilever against 10.5 kips downwards due to the structural weight within the trib area of the column. In real life, the detrimental dead load could easily have been underestimated by a small margin, lifting the column under dead load alone. However, the software would show no net uplift at target reliability.
I'm curious as to whether anybody's come across this, and what method you would use to meet the standard of care. Is it appropriate to design to 0.9D_resisting + 1.2D_acting (equivalent FS = ~1.3)? Perhaps 0.9D_resisting + 1.4D_acting (FS = ~1.5)? Better to use a foundations approach with acting vs resisting forces at FS=2? I imagine this FS is intended to consider variability in soil weights, which are much higher than variability of dead load. Is it possible to perform such a check in a single software model?
Excited to hear some thoughts on this. Feel free to comment on just part of this very dense post.
------------------------------
Christian Parker P.E., M.ASCE
Structural Project Engineer
Washington DC
------------------------------