    Hello,

    We design and install meteorological guyed and self-supported masts. Most of our masts have service lives of 1 to 3 years. Since we consider them risk category I, we use a 300-year mean recurrence interval. However, we are curious to know whether it is an acceptable practice to assume much lower return periods, given that the structure is temporary and has a maximum life of 3 years.

    For example, before accounting for the importance factor and the wind load factor, can we use 25-year mean recurrence interval instead of 50, then apply the wind load factor and the importance factor?


    #ASCE7
    #WindandWindLoads

    ------------------------------
    Assem Abozeed A.M.ASCE
    Lead Engineer
    Kilolima
    Maadi
    ------------------------------


  • 2.  RE: An inquiry about decreasing the return period of the design wind speed for temporary structures
    Best Answer

    Posted 11-01-2023 01:31 PM

    Assem

    This is an excellent question, that has been considered, but not answered many times by the ASCE 7 committee.  There are two relevant points of view:

    1- Since a temporary structure will exist only for a limited time period, if it is designed for the same load return periods as permanent structures, it will have a much lower risk of failure, during its lifetime.  This is true and an argument for using reduced return period loads for design.

    2- If a person enters a temporary structure (or stands next to it), that has been designed for reduced return period loads, then that person will be at higher risk of injury while in (or next to ) the temporary structure than if that person were in (or next to) a permanent structure.  This argues that to provide equal safety to occupants, all structures should be deisgned for the same return period loads.

    A third point is that many structres that are intended to be "temporary" end up being used far beyond their expected life times.  For example, following the great San Francisco earthquake of 1906, government agencies provided shelter for homeless residents of the City in the form of inexpensive, modular wood frame buildings, the then equivalent of "FEMA Trailers."  Not surprisingly, some of these stuctures are still in service today,nearly 120 years later. As a society, we have little control over the temporary nature of construction.

    As you are likely aware, ASCE 37 provide loads for design of structures during construction that are substantially reduced from tthe requirements for permanent conditions.  THese loads are reduced in part becasue the time frame of the construction period is short, but also because construction sites have relatively few occupants, there is an implied risk accepted by construction workers and sites can be shut down if a large storm is known to be approaching.  It is therefore not applicable to the types of structures you are working with.

    The ASCE 7 committee will continue to wrestle with temporary structures and may some day have more definitive guidance.



    ------------------------------
    Ronald Hamburger, SE
    Consulting Principal
    Simpson Gumpertz & Heger
    ------------------------------



  • 3.  RE: An inquiry about decreasing the return period of the design wind speed for temporary structures

    Posted 11-02-2023 08:04 AM
      |   view attached

    A temporary structure sloped asbestos sheet roofing plan is given attached. When wind is blowing the roof is flew away. Suction pressure is came into play. Wind was entered through the open side which did the harm.



    ------------------------------
    Alex Thomas R.Eng, C.Eng, M.ASCE
    Senior Site Engineer
    Geo Structurals Pvt Ltd
    CochinAlexThomasR.Eng, C.Eng, M.ASCEIndia
    ------------------------------



  • 4.  RE: An inquiry about decreasing the return period of the design wind speed for temporary structures

    Posted 04-22-2024 12:44 PM

    Ronald,

    Thank you so much for this very helpful response!

    We looked into the ASCE 37-14 and the Eurocode EN-1991-1-6. 

    Our met masts usually serve in unpopulated areas in deserts or mountainous regions. Their service life is usually less than 3 years. Having looked at the codes, we will use the basic wind speed reduction factor of 0.9, following the ASCE 37.

    Our structures are usually Risk Category I; their construction periods are usually a few days per structure. During construction, we closely observe weather forecast since our installers work at heights and must stop working when the wind gusts reach 13 to 15 m/s. Given those facts of very short construction periods and the close weather monitoring throughout, we believe that adhering to a Risk Category II during construction could be an overkill in our cases. 

    If you have comments or opinions on this approach, we would be grateful to receive them. Thank you for pointing us in the right direction.



    ------------------------------
    Assem Abozeed A.M.ASCE
    Lead Engineer
    Kilolima