Integrated Buildings & Structures

 View Only
  • 1.  PRECAST DIAPHRAGMS, ASCE 7-16, 14.2.4.3

    Posted 12-12-2019 09:43 PM
    In a high seismic area, using the Reduced Design Option and High Deformability Elements (HDE) for precast diaphragm connectors, ASCE 7-16, 14.2.4.3.3 says that the connectors have to "tension deformation capacity" per 14.2.4.6.7 of greater than 0.6-inches.

    How would I determine "tension deformation capacity"?

    What procedure is the 14.2.4.6.7 reference pointing to?  This section does not exist in my printing of ASCE 7-16 or in any errata, supplement or reference code I can find.

    ------------------------------
    David Stierwalt P.E., M.ASCE
    Reid Middleton, Inc
    Anchorage, AK
    ------------------------------


  • 2.  RE: PRECAST DIAPHRAGMS, ASCE 7-16, 14.2.4.3

    Posted 12-13-2019 10:10 AM

    David,

    Tension deformation capacity is determined in 14.2.4.4.7.

    There is probably a typo with this cross reference.



    ------------------------------
    Gustavo Escorcia Ing., P.E., M.ASCE
    Structural Engineer
    STV / Ralph Whitehead and Associates
    North Chesterfield VA
    ------------------------------



  • 3.  RE: PRECAST DIAPHRAGMS, ASCE 7-16, 14.2.4.3

    Posted 12-16-2019 11:00 AM
    Is there a published document that classifies or reports these backbone curves for precast diaphragm connection details?

    ------------------------------
    David Stierwalt P.E., M.ASCE
    PRINCIPAL
    Reid Middleton Inc
    Anchorage AK
    ------------------------------



  • 4.  RE: PRECAST DIAPHRAGMS, ASCE 7-16, 14.2.4.3

    Posted 12-19-2019 07:10 PM
    Edited by Tirza Austin 12-19-2019 07:12 PM

    @David Stierwalt

    I have been asked to share the following response on behalf of the chair of the ASCE 7 Seismic Subcommittee: 

    Thank you for pointing out the issue of trying to determine the "tension deformation capacity, as determined in Section 14.2.4.6.7."  Actually, you uncovered an erratum (which also exists in Sections 14.2.4.3.1 and 14.2.4.3.2) for the section being referenced.  The actual section that was intended to be referred to is 14.2.4.4.7.  You'll find the appropriate requirements to determine "tension deformation capacity" in this section.  Thank you, again, for pointing this out.

    DISCLAIMER: Reliance on the contents of this communication is solely and completely at your own risk; therefore, we advise you to exercise a reasonable degree of caution in your use of any information or advice contained herein. This information is provided for general informational purposes only and is not intended in any fashion to be a substitute for professional consultation. Under no circumstances does ASCE, its affiliates, officers, directors, employees, or volunteers warrant the completeness, accuracy, or relevancy of any information or advice provided herein, or its usefulness for any particular purpose. ASCE, its affiliates, officers, directors, employees, and volunteers expressly disclaim any and all responsibility for any liability, loss, or damage that you may cause or incur in reliance on any information or advice provided herein.



    ------------------------------
    Tirza Austin
    Manager, Online Community
    American Society of Civil Engineers
    1801 Alexander Bell Drive
    Reston, VA 20191
    ------------------------------