Drainage and Storm water Networks under Road Pavement

  • 1.  Drainage and Storm water Networks under Road Pavement

    Posted 04-06-2019 07:41 PM
    Edited by Tirza Austin 04-11-2019 04:37 PM
    We are currently building a road network, the terrain is similar to Texas. i.e. Black Cotton Soil.

    The current design depths of Foul Sewer Network at the deepest ins 10m. storm water is 6- 8 m deep with 3 Lift stations.

    However, an alternative design limits the depth to a maximum of 4 meters but 12 Lift stations in order to save excavation.

    What is the best option to choose? 

    I presume most of the countries are now moving away from lift stations and preferring deeper networks for long-term benefits.

    If anyone has experienced this before or involved in these kind of projects at any level, your input is really appreciated. 

    Thank you. 


    ------------------------------
    Kalyan Emandi
    Sr.Project Engineer
    ------------------------------


  • 2.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-07-2019 08:44 AM
    Edited by Tirza Austin 04-11-2019 04:37 PM
    Kalyan,
      What does your economic analysis indicate?

    ------------------------------
    James Justin Mercier, P.E., CFM
    Life Member ASCE
    Sr. Life Member IEEE
    Austin Texas
    512-442-4016
    ------------------------------



  • 3.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-07-2019 07:43 PM
    Edited by Tirza Austin 04-11-2019 04:37 PM
    Hi James,
    At this point with lead times of different components with 12 lift stations makes it more difficult with respect to time and cost.
    The first solution is cumbersome land requires more resources including backfill material . However all of it included equipment are locally available and can be done faster with right strategy in place . Barring 3-4 months of rains which is the same constraint for both the solutions

    Regards,

    Kalyan Emandi
    +9689627765





  • 4.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-10-2019 10:28 PM
    Edited by Tirza Austin 04-11-2019 04:37 PM
    You are correct that lift stations are to be avoided whenever possible.  You can expect extensive utility trench settlement with the first solution.  It is very difficult to achieve adequate compaction in such deep trenches.  The depths you are contemplating could well compromise the pavement structure.  However, I have recently dealt with that problem by using a geogrid (Triax 140 or 160), and 6-8 inches of flex base over the backfill.  We used good bedding material under and around the pipe but used the native soil (expansive clay) for the backfill compacted as well as possible.  Trench boxes were used for safety and to keep the trench as narrow as possible.  That really cuts down on cost as decent backfill is getting harder to find and more expensive in Texas.

    ------------------------------
    James Anderson, MASCE
    Principal
    Anderson Consulting
    North Richland Hills, TX
    817-946-9943
    James
    ------------------------------



  • 5.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-08-2019 07:29 AM
    Edited by Tirza Austin 04-11-2019 04:37 PM
    Did you consider tunneling?

    ------------------------------
    Robert Arias M.ASCE
    Arias and Associates Inc
    San Antonio TX
    (210) 308-5884
    ------------------------------



  • 6.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-08-2019 09:49 AM
    Edited by Tirza Austin 04-11-2019 04:37 PM
    With manholes every 40 meters tunneling seems out of question and more costly.

    ------------------------------
    Kalyan Emandi
    Sr.Project Engineer
    ------------------------------



  • 7.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-11-2019 04:18 PM
    Edited by Tirza Austin 04-11-2019 04:37 PM
    My suggestion is that limiting the number of lift stations would be preferable, since you invite less long-term maintenance costs.  Have you considered using a one-sack sand slurry mix (at least to fill to a level of a couple of meters above the pipe) to avoid​ deter settlement issues? The material cost may be more, but you eliminate the need for compaction and testing in/around the pipe.  And the one-sack can be excavated with a backhoe if needed to access the pipe later.

    ------------------------------
    Eric Sosnowski M.ASCE
    Bluffton SC
    ------------------------------



  • 8.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-11-2019 05:10 PM
    Edited by Tirza Austin 04-11-2019 05:10 PM
    We haven't considered one sack sand slurry. I will research it. If you can elaborate a bit more. It will be very helpful. Thank you! 




  • 9.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-11-2019 06:05 PM
    Edited by Tirza Austin 04-11-2019 06:04 PM
      |   view attached
    This should give you a bit more information.  One sack slurry, or flowable fill, or controlled low strength material (CLSM) can be used by adding cement to onsite soils, provided they have proper gradation, as indic dated in the cut sheet.  My experience is more in having the slurry delivered from a concrete supplier, who has a mix design in place for simply adding one sack of cement to sand, and adding water that allows the material to flow wherever you need it.  Hope this helps. 

    ------------------------------
    Eric Sosnowski M.ASCE
    Bluffton SC
    ------------------------------

    Attachment(s)

    pdf
    nsbfactsheet.pdf   272 KB 1 version


  • 10.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-12-2019 07:56 AM
    Edited by Tirza Austin 04-12-2019 07:55 AM
    I was not able to view the attchment, so I don't know if it addresses the issue of pipe floating when using flowable fill materials, but that is something you need to address. There are many different methods of securing pipe to hold it in place until the fill sets, but the uplift forces are signuficant so you must plan on some method of anchoring the pipe.

    ------------------------------
    James Gernand EIT,A.M.ASCE
    Redwood City CA
    (650)544-0799
    ------------------------------



  • 11.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-12-2019 10:51 AM
    Edited by Tirza Austin 04-12-2019 10:50 AM
    Since we're talking about stormwater pipe, I assume RCP is being used.  Unless the pipe is below groundwater level, hydraulic uplift isn't likely.

    ------------------------------
    Eric Sosnowski M.ASCE
    Bluffton SC
    ------------------------------



  • 12.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-12-2019 11:13 AM
    Edited by Tirza Austin 04-12-2019 11:12 AM
    The pipe is below ground level. Twin walled HDPE pipe. Which is now being used quite frequently. Especially in Europe. 

    The connections, pipe lifting and installation is much easier and faster than regular RCP .

    ------------------------------
    Kalyan Emandi
    Sr.Project Engineer
    ------------------------------



  • 13.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-12-2019 11:13 AM
    Edited by Tirza Austin 04-12-2019 11:13 AM
    Eric Sosnowski's suggestion regarding a flowable fill in the pipe area is a good one.  If you have access to an inexpensive supply of fly ash, the flowability can be improved without adding excessive water to the 1-sack mix.  You must be careful not to "float the pipe" while it is being applied.  The backfill will still be "diggable" even with the addition of Class C ash.  You may find it too expensive to use flowable fill for all the backfill.  That is why I suggested using geogrid and flexbase over the natural material in order to reduce stress on the pavement following trench settlement.

    ------------------------------
    James Anderson, MASCE
    Principal
    Anderson Consulting
    North Richland Hills, TX
    817-946-9943
    James
    ------------------------------



  • 14.  RE: Drainage and Storm water Networks under Road Pavement

    Posted 04-12-2019 11:36 AM
    Edited by Tirza Austin 04-12-2019 11:35 AM
    Hi James, Thank you for the information. I am still looking into it. We do not have access to the material (fly-ash). Which in a sense kills the optimization of resources and time.

    ------------------------------
    Kalyan Emandi