Peer-to-Peer Standards Exchange

 MWFRS Wind Pressures on Hipped End - Wind Parallel to Ridge

  • ASCE Standards
  • ASCE7
Chris Rosencutter's profile image
Chris Rosencutter posted 08-24-2023 04:02 PM

This question really applies to all ASCE 7 versions.  The MWFRS roof pressure Coefficients are determined from Figure 27.3-1.  In the case where the wind is parallel to the ridge, and the hipped end has a slope of ≥ 10°, do we consider the hipped end "Normal to Ridge" or "Parallel to Ridge"?  For example, in the image below, is the hipped end (The Green color) considered normal to ridge or parallel to ridge?  Also, is the slope based upon the sloped end or is it the slope of the main roof?  My opinion is that it is the slope of the hipped end and that it would be considered "Normal to Ridge", but I'm not 100% sure.  

Thanks,

Chris Rosencutter

Keith MacBain's profile image
Keith MacBain

Hi Chris,

My interpretation is that terms normal or parallel to ridge pertain to the wind direction, not the surfaces.  If pressed for an answer, I believe I'd characterize the green surface as normal to the ridge, but I believe that's not how one enters Figure 27.3-1.  For your image the wind is parallel to the ridge, and if it were 90 degrees from what you show, it would be normal to the ridge.   

However, by this interpretation it appears that Fig 27.3-1 does not explicitly consider all faces of a hip roof. which might be the crux of your question.  In particular, when wind is parallel to the ridge, one enters the second table you show and does not find a value for a windward roof surface (i.e., your green surface).  Hmmm, not sure there.  I’d suppose the programmers for the software you use also wrestled with this and decided to go back to the first table you show, even though wind is not normal to the ridge as the heading indicates. 

This means that for the green face you’d use the value(s) for the windward face in the first table at whatever angle and h/L you have, even though the wind is actually parallel to the ridge (i.e., contrary to the heading of normal).  This also applies to the leeward face, which is hidden in your figure.  For the sides of the roof (pink, gray, and brownish) you’d return to the second table because the wind is indeed (still) parallel to the ridge.  I believe that’s what I’d do. 

Hope this helps,

Keith

Keith MacBain's profile image
Keith MacBain

Chris,

Another approach is that you could ignore the pitch of the green surface entirely and follow only the second table when wind is parallel to the ridge.  This means that the green surface would receive the same pressure as say the pink surface depending on the distance from the windward edge.  How realistic or conservative this is would depend on the angle.  In other words, if the green surface is very steep it would tend more toward a windward face (first interpretation) whereas a flatter pitch may approach this second interpretation.  

A similar difficulty arises with wind normal to the ridge, in which case the green surface is neither windward or leeward.  Naturally one can divide the surface along an extension of the ridge line but here again, this is not given explicitly.  Hopefully an ASCE person can give us a definitive answer for all angles and directions.  

Hope this helps,

Keith

Chris Rosencutter's profile image
Chris Rosencutter

Hi Keith MacBain,

Thanks for the feedback.  In this case I am the software developer for the Wind software and that's the reason I'm trying to get clarity.  I can see both sides of the argument and am hoping to get a definitive answer.  Mr. Ronald Hamburger from the ASCE 7 wind committee frequently responds to questions on this site, and so I'm hoping that he might offer some insight on this one.  

Thanks,

Chris Rosencutter

www.mecaenterprises.com