Per Section 29.4.3, roofs, and other portions of the MWFRS must be designed for two cases:
1- The case where collectors are present. The loads from section 29.4.3 are applied to the roof over the footprint of the panels, and the standard roof wind loads are applied elsewhere.
2- The case where collectors are not present, in which case the standard loas are used.
------------------------------
Ronald Hamburger, SE
Consulting Principal
Simpson Gumpertz & Heger
------------------------------