ASCE 7 has moved away from drift checks based on a fixed ratio of design wind loads. The motivation for this is understandable. As the commentary (Section CC1.2 in ASCE 7-10) suggests, different projects may have different risk tolerance for serviceability failure. For example, I am working on a Risk Category II building which has hand-painted frescoed interiors. Excessive drift would be a real issue for the artwork, so we used a 50-year mean recurrance interval (MRI), bringing the serviceability loads to roughly 0.6W.
However, note f in IBC (2018) Table 1604.3 allows for a standard
0.42 factor on ultimate C&C loads to check drift, equivalent to roughly a 10-year MRI. This is consistent with the
0.7 factor on ASD wind loads from the Commentary to ASCE 7-05 Appendix C, which was removed in ASCE 7-10. With the intent of ASCE 7-10 and later to calculate serviceability wind loads based on a selected MRI, the IBC provision seems increasingly like a loophole: I can't imagine an SER or client specifying an MRI
less than ten years. Is there any discussion of removing this note from IBC? Should there be? What are your opinions on using a fixed coefficient versus a mean recurrance interval approach?
This article in Structure Magazine touches on this:
https://www.structuremag.org/?p=17439#ASCE7#ASCE7-10#ASCE7-16#ASCE7-22#WindandWindLoads#LoadCombinations------------------------------