I am looking for some clarification regarding the seismic load calculation for a pipe support anchorage design. The scenario is a pipe submerged in a water-filled concrete basin which is located in a high seismic region and experiences sloshing. In such a scenario, I understand that the pipe and its supports should be acted upon by the following 3 seismic loads:<o:p></o:p>
- The 1st seismic load acting on the pipe and its supports is the seismic response of the pipe itself. This load is calculated per Chapter 13 of ASCE 7-16, Table 13.6-1 of which provides R and Ω0 factors for different piping systems. <o:p></o:p>
- The 2nd seismic load acting on the pipe is the impulsive load of water sloshing. The impulsive load is calculated based on Chapter 15 of ASCE 7-16, Table 15.4-2 of which provides R and Ω0 factors for different tanks.<o:p></o:p>
- The 3rd seismic load acting on the pipe is the convective load of water sloshing. The convective load is calculated based on Chapter 15 of ASCE 7-16 with an R=1.5 (which is implicitly included in Eqn. 15.7-6). I have not found an Ω0 factor in ASCE 7-16 for the convective loads (if there is one and I have missed it, I would appreciate it if you could point me to it for my information).<o:p></o:p>
<o:p> </o:p>
Specifically for the design of the pipe support anchorage: the seismic load from the seismic response of the pipe itself (Seismic Load #1 listed above) needs to be multiplied by the Ω0 factor provided by Table 13.6-1; do the impulsive and convective loads on the pipe need to be multiplied by an Ω0 factor too? If yes, which Ω0 factor would be appropriate in that case?<o:p></o:p>
Thanks,<o:p></o:p>
Kostis Oikonomou
#ASCE7-16#Seismic#LoadCombinations------------------------------
Konstantinos Oikonomou Ph.D., P.E., M.ASCE
Senior Engineer I
Mesa AZ
------------------------------