A Plan Reviewer recently commented concerning my wind calculations using ASCE 7-10 (the adopted standard in this jurisdiction). As is the case with many engineers designing in wood, to use ASD I apply the 0.6 load factor to qz, in lieu of applying it in the Basic Load combinations. To me, this makes the loads much easier to track to the foundations. The Reviewer Stated:
"The minimum design wind loading for the main wind-force-resisting system and components & cladding shall be not less than 16 lb/sq.ft. (and some allow minimum 8 lb/sq.ft. for roofs). Page 5 shows component & cladding loadings as below 16 psf for 26 of the 44 cases, which is unacceptable, revise to comply."
Another issue is the proper application of the minimum wind loads. Does every calculated pressure design pressure have to exceed the minimum, or is the minimum a separate load check like Components & Cladding.
Thanks to the forum in advance.
------------------------------