It's seem that horizontal irregularities geometric stability is there but a cutouts necessitate to reduce moment at the centre and avoiding tilted. This is my humble opinion. I wish to hear from you
Alex Thomas MIE REng CEng M ASCE
Alex Thomas R.Eng, C.Eng, M.ASCE
Senior Site Engineer
Geo Structurals Pvt Ltd
CochinAlexThomasR.Eng, C.Eng, M.ASCEIndia
Sent: 04-27-2023 03:08 PM
Subject: ASCE 7 Horizontal irregularity #5 - Nonparallel system
If hand calculations are done such that the stiffnesses of the shear walls are considered as well as the location and direction of those stiffnesses AND the center of force along with the eccentricities of the load (both actual and minimum) are taken into account, what else must one do to "consider the 3D behavior of the system"? IMO, if the roof diaphragm were considered as semi-rigid, i.e., the stiffness of the diaphragm considered, then I would totally agree with a 3D computer model to solve the problem. Otherwise, I don't see how one can do anything more to "consider the 3D behavior of the system". Not being critical for you have much more knowledge and experience in this area than I do. I'm sincerely curious.
Thank you,
Bill Allen P.E., S.E., M.ASCE
Allen Designs
Mission Viejo CA
Sent: 03-09-2023 12:08 PM
In my opinion, a 3D model is not required because this building has a flexible diaphragm. However, even if hand calculations and statics are used ot determine the forces on the walls, one has to consider the 3D behavior of the system.
Sent: 03-08-2023 02:52 PM
Great! Agree on the applications of loads.
The follow-up question would be, is it required to be analyzed using 3D model per ASCE 7-16, 12.7.3?
12.7.3 states that for horizontal irregularity 1a, 1b, 4, and 5, a 3D model is required; the only exception is provided for a flexible diaphragm structure if it has horizontal irregularity 4 (out-of-plane offset).
Manhin Lee Aff.M.ASCE
Plan Check Professional
City of Fremont
Fremont CA
Sent: 03-08-2023 02:19 PM
The structure you show in plan would be considered by most engineers to have horiozntal irregularity type 5. It should be analyzed and deisnged for 100% of the forces in Direction X combined with 30% of the forces in Direction Y, and 100% of the forces in Direction Y combined with 30% of the forces in Direction X.