To make it simple, let's use the following assumptions:
- Ground snow ASCE 7-16 = 35 psf.
- Ground snow ASCE 7-22 = 50 psf.
Check service level roof pressure for an identical 4ft high snow drift.
- Density = 0.13pg +14
- 18.55 pcf (ASCE 7-16)
- 20.5 pcf (ASCE 7-22)
- Drift pressure = load factor x height x density.
ASCE 7-16
- Service level drift pressure = 1.0 x 4 x 18.55 = 74.2 psf
ASCE 7-22
- Service level drift pressure = 0.7 x 4 x 20.5 = 57.4 psf
Since the majority of the density equation is determined by a constant, an identical height drift is significantly lighter using ASCE 7-22. It is possible that previous codes were approximately 30% heavy on the assumed snow density. But, I have not heard that argument.
Jacob Trapp
Fond Du Lac WI
Sent: 06-30-2025 06:36 PM
Subject: ASCE 7-22 Snow Load Updates
The relationship between snow density and ground snow load does not change between the older 5-year MRI and newer reliability targeted loads. Therefore adjustment of the load factor for ASD is not required.