This message was posted by a user wishing to remain anonymous
In the errata issued on July 25, 2024, footnote l was removed; however, there does not appear to be any explanation in the commentary clarifying the reason for disallowing OCCs. In ASCE 7-16, OCCs were permitted for buildings per Section 12.2.5.6.2, with limitations tied to roof dead load. The commentary referenced limits on individual column axial load, but this did not appear to constitute a prohibition of OCC systems.
Additionally, Table 15.4-1 in ASCE 7-22 still permits Steel Ordinary Moment Frames in SDC D, E, and F, subject to certain limitations. Section 15.4.1 also allows the use of either Table 12.2-1 or Table 15.4-1 for nonbuilding structures similar to buildings. This appears to create a potential inconsistency between the two tables.
Historically, OCCs have been widely used in the industry for structures such as carport canopies, shade structures, and similar applications. Many of these structures are not governed by seismic design. Disallowing OCCs lead to additional requirements per AISC 341-22, including higher ductility demands, protected zone requirements, and more stringent connection detailing, which doesn't make sense since wind load is governing the design.