Not sure about
COSP, but I suspect an engineer is within their rights to put the requirement in the contract documents, and a contractor is within their rights to ask for a change if that engineer later realizes the loads are unconservative at some locations. Regardless, it's not practical, and AISC has repeatedly made the plea for designers to show actual loads instead. Here is an article (co-authored by Muir and probably similar to the webinar Steven mentions) from the Nov. 2019 issue of
Modern Steel Construction which discusses the issue:
https://lsc-pagepro.mydigitalpublication.com/publication/?m=7946&i=626249&view=articleBrowser&article_id=3503098&pre=1Chad, I'm curious as to what sort of disputes you see coming up? Have you seen fabricators underbid a job relative to max. uniform load when it is required on the bid documents?
------------------------------
Christian Parker EIT, A.M.ASCE
Structural Project Engineer
Washington DC
------------------------------
Original Message:
Sent: 07-22-2021 12:46 PM
From: Chad Morrison
Subject: Using the maximum total uniform load table to derive design loads
Structural drawings and specifications often note that one half (or 0.67) of the maximum uniform load table value should be used for connection design when no reaction is given. This is widely accepted as a conservative and useful approach by most engineers. This approach is problematic for short beams when the value derived can be too high for practical connection design or for sections not listed in the table.
Does using the uniform load table conform with the AISC Code of Standard Practice which requires design loads be given? Is there a source available that addresses the issue in a way that resolves disputes that arise from its application?
------------------------------
Chad Morrison P.E., M.ASCE
Professional Engineer
Greenville RI
------------------------------