Dear Kirk,
I believe the main issue is the absence of shop drawings. It's a liability issue: Once we touch an existing structure, we become liable to its performance, including issues that might be exisisting in its current condition before we even touched it. When it comes to rehabilitation/ alteration work, design notes should start with full information about the existing structure. Design notes should, as always, be able to stand in a court of justice, if need be for whatever reason (can be due to some other party's fault) .
If I was to do alterations to DTs, I would need shop drawings showing:
- Strands profile; number, configuration (straight/ one point depression/ two point depression), de-bonding
- Ultimate strength (270 ksi?)
- Low relaxation or stress relieved?
- Jacking force
- Concrete strength at release (f'ci).
- Concrete strength at 28 days (f'c) + site inspection/ testing to confirm that f'c is met or exceeded.
Drains can be added at DT ends, centered at the joint between two DTs to minimise the reduction to cross section.
Run design using a trusted prestressed / precast design program: contact PCI or CPCI
In the case you have: There is problem with the loading too: Parking garages LL= 50 psf. Retail LL, if I remember correctly, is double that. Besides, there is added thickness to topping to make up for the difference between parking and retail finished surface. Most likely, the original capacity will be exceeded, unless it was designed with ample extra capacity, which is very unlikely.
If was given a project like this one, I would play it safe as noted above.
------------------------------
Neil Kazen, M.Eng., M.Sc., P.Eng.
FASCE, FCPCI, FEC,
Retired Structural Engineering Manager, Transportation Division, SNC-Lavalin
Toronto, Ontario, Canada
------------------------------
Original Message:
Sent: 10-11-2018 05:42
From: Reza Mokarram Aydenloo
Subject: Retrofit of Precast Double Tee Floor System
Dear Kirk Ellison,
I have good information about retrofitting old buildings. I'm glad to be able to help you.
Can you provide information details on why retrofitting is not enough?
Please provide a few photos of the project and architectural plans.
Depending on the project, a suitable method can be provided.
------------------------------
Reza] [Mokarramaydenlou Ph.D., P.E., C.Eng, S.E., M.ASCE
Structural Engineering and Seismic rehabilitation Consultant
Mokarramandpartners LLC
Original Message:
Sent: 10-10-2018 18:28
From: Kirk Ellison
Subject: Retrofit of Precast Double Tee Floor System
An owner would like to convert the ground floor of an empty two story retail building to a grocery store and food court. The ground floor consists of 10'-0" wide x 24" deep precast double tees spanning between precast inverted t-beams, with a 2'-6" crawl space underneath. The existing floor has few openings/penetrations and those that are there were accommodated in the original design and construction in the mid '80s.
The grocery layout requires a significant amount of drains, plumbing, trench drains, sloped slabs, etc. I need some technical assistance regarding retrofit of existing precast double tees. Are there any options other than removing a large portion of the existing floor and replacing with a cast-in-place solution? Original manufacturer is not in business and shop drawings do not exist. I have warned Architect and owner that cutting of precast members is not advisable.
Any precedents or advice?
Thank you in advance.
------------------------------
Kirk Ellison P.E., M.ASCE
Principal
Ellison Gage & Associates, PLLC
Plano TX
9723548855
------------------------------