The modulus of rupture is going to vary depending on the glass temper, and E=10400ksi per the ASTM E1300.
Sent: 12-12-2024 04:39 PM
Subject: Reference for calculating the stress in the interlayer of laminated glass?
The hardware vendor will typically have technical data available for a glass shoe or button.
Here is one link with publicly available information that might be helpful.
https://www.crlaurence.com/technicalreference/findByProductCategory/search?s0Category=RailingWindscreenSystems&s1Category=E01_HR&s2Category=E01B_HR&s3Category=&s4Category=&q=E01B_HR%3Arelevance%3Agroups%3AEngineering%2B%2526%2BTest%2BReports
Looking at some past calcs, for 3/4" laminated glass, I used a modulus of rupture of Fr = 24000 psi and a factor of safety of 4. The elastic modulus is E = 10000 ksi. Be sure to check with the glass manufacturer or job specs. The interlayer should not control the design. The glass should crack and remain adhered to interlayer after failure.
I recommend always using a top rail on glass panels. This ensures the panels deflect together and do not pinch fingers in the joint (differential deflection cannot exceed the thickness).
Chad Morrison P.E., F.ASCE
Professional Engineer
Greenville RI
Sent: 12-11-2024 12:15 PM
I wanted to show the tensile stress of the interlayer had a safety factor of at least 4.0 per code for handrail live loads.
Brenda Moore P.E., M.ASCE
President
BLM Consulting Engineers, Inc.
Midlothian VA
Sent: 12-11-2024 08:47 AM
I don't think MEPLA has an option for that, what are you looking to do with the interlayer stress?
Renn Henry, PE
Staff Engineer