That article references AISI S240-15, B1.1. B1.1-B1.1.2 read as follows:
B1.1.1 Application of Live Load Reduction on Wall StudsFor the purpose of calculating the design axial load on a wall using floor live load reduction requirements in accordance with the applicable building code, the tributary area of the wall shall be limited to the floor area assigned to the individual wall framing members.B1.1.2 Application of Wind Loads on Wall Studs in the United States and MexicoIn the United States and Mexico, the design of the wall studs shall be based on the following design wind loads:(a) Combined bending and axial load effect based on Main Wind Force-Resisting System (MWFRS) wind loads.(b) Bending load effect based on Components and Cladding (C&C) wind loads.(c) Deflection limits based on 42% of Components and Cladding (C&C) wind loads with no axial loads.AISI S240 B1.1.1 refers to the applicable building code, usually the IBC in the US. The IBC allows the live load reductions for any material. This is not a special case applying only to steel studs.
In paragraph B1.1.2, AISI is not creating any special consideration for steel stud walls. They are just summarizing the load cases that need to be checked and how the relevant ASCE 7 and IBC provisions apply to stud walls. The effects of the wind on the MWFRS need to be checked on any studs that are part of the MWFRS (often shear walls). But also because the exterior wall studs are part of the curtain wall system, those studs also need to be checked for Component and Cladding wind loads. The 42% factor is used because wind loads after ASCE 7-10 are strength level loads and comes from IBC 2018 Table 1604.3, footnote f.
These provisions apply equally to wood construction or any other material, where elements of the structure are both part of the MWFRS and are the building "curtainwall" or exterior. (Its typical to refer to steel studs on building exteriors as curtainwall but I have not heard it applied to wood construction.)
I teach both wood and CFS design class at the graduate level and I am Chair of the ASCE/SEI Committee on the Performance of Wood Structures. I was in full-time design practice for 20 years before entering academia.
------------------------------
William Kirkham Ph.D. Ph.D.,M.ASCE
The University of Kansas
Overland Park KS
------------------------------