Jordan,
The allowable lateral bearing capacity and the passive earth pressure are very different things. The passive pressure is the maximum pressure that can be developed on an earth-retaining structure before failing by shearing a displacing a wedge of soil. It can be adapted to a pile but the theories were developed for walls. More importantly, it represents a limit state condition, so it is not an allowable pressure.
For the IBC post and pole method you want to use, there are presumptive lateral bearing pressure values in Table 1806.2. However, what you need to understand is that allowable bearing pressure is not a physical property of the soil. It is a lumped parameter that tries to account for shear strength, deformation, and, to an extent, foundation geometry. The presumptive values in the code are lower bound values of what is already a conservative approximation and should not be used for significant structures because they are excessively conservative.
A better approach would be to seek guidance from the project geotechnical engineer, assuming the <g class="gr_ gr_17 gr-alert gr_spell gr_inline_cards gr_disable_anim_appear ContextualSpelling ins-del multiReplace" id="17" data-gr-id="17">geotech</g> has adequate foundation engineering capabilities (as opposed to just sampling and testing) to field this sort of question. A soil-structure interaction approach (p-y curves and such) will typically provide a more rational prediction of soil behavior and forces internal to the foundation.
I hope this is helpful.
Richard J. Driscoll P.E., M.ASCE
Consulting Engineer
Lebanon, NH / Washington, DC