Dear Shashank,
Before looking into the next construction procedure, we need to understand why the deflection differential is so large? Is that due to some deficiency in the girders? Last time I had something like that (it was a different kind; prestressed precast girders) it turned out that some strands were not stressed. The girders were discarded.
In this case, what possibly caused it? Slippage in the joints coupling the girder pieces? Or inferior material? Or wrong plate thicknesses? Or …?
By the way, using so many pieces per girder, relies heavily in the connections. The connections at 5m from the centre will be carrying 97% of the maximum bending moment; a high risk situation.
On the other hand, could the camber be faulty at manufacturing?
Do the girders have the required strength? If that was my bridge, I would have demanded performing load/deflection test.
If the above was checked and found safe; say, the problem was only in faulty camber at production, then construction procedure can be discussed.
The 5 steps you listed are reasonable, except that step 1 needs to supported by analysis: on a 3D model, check the effect of the girders that were jacked up on site, being loaded DOWN by the force that was used in jacking. That's because those girders will try to go back to their original shape before site-jacking. On that 3D model, check the stresses and deflections of the concrete slab as the released girders will try to rebound back; adding to the stresses in the slab.
If that passed the 3D analysis check, then the remaking 4 steps you listed are good. In my steel bridge construction, I made sure that the whole concrete deck was poured before any part of it was set; for a long bridge, I used concrete cure retardant so that setting happened after the end of the whole pour.
Good luck.
------------------------------
Neil Kazen, M.Eng., M.Sc., P.Eng.
FASCE, FCPCI, FEC,
Retired Structural Engineering Manager, Transportation Division, SNC-Lavalin
Toronto, Ontario, Canada
------------------------------