Colton,
I have a couple of questions:
1. Please clarify what you mean by "initial softness is more than expected". Is the entire frame settling? Is the truss deflecting more than expected? Both? Can you give us an idea of the magnitude of the difference between expected versus actual (less than 5%, more?)
2. If the entire frame is settling, your supposition may be correct. If it's more localized, can you tell if it is localized to a truss member or if the connections are allowing the most movement?
3. Have you received the 3rd party testing reports indicating all connections, and especially the moment connections, have been fully welded? (I once received a phone call that a connection I had designed was "failing", only to discover that the designed moment connection had not yet been welded in the field.) Similarly, do the foundation reports confirm bearing capacity was met or exceeded?
4. Is the connection as detailed and the connection behavior assumed via modeling match? For example, are the truss connections in your analysis model designed as fully pinned (and the moment connections as fully fixed), and were the connections confirmed to be detailed this way, especially if this was a delegated design (common in USA East Coast)? Since we have to idealize connections in our models, I usually find that the actual "real" behavior in both to be somewhere in between, especially when it comes to deflection.
5. Was the construction sequencing/loading on the truss as expected? Are there any splices in the truss that could be contributing or unusual sequencing that could affect behavior? (For an example, if your truss is supporting a 4 story transfer column and the contractor decides to pour concrete on top floors first, this means the composite action you may have been counting on for the truss member is not in place when the upper floor concrete loads are applied and would result in higher deflections that if the <g class="gr_ gr_2652 gr-alert gr_spell gr_inline_cards gr_run_anim ContextualSpelling ins-del" id="2652" data-gr-id="2652">truss</g> level was poured first.)
------------------------------
Stephanie Slocum P.E., M.ASCE
Founder
Engineers Rising LLC
------------------------------