It's been a while since I had to deal with high temperatures on foundations (first 7 years out of school dealing with steel mill equipment....), but I'll give it a shot:
- extreme high temperatures - I don't recall the threshold - can deteriorate the concrete itself regardless of the amount of rebar. I don't suspect you're near that temperature. Think building fires.
- spalling of the concrete surface down to the layer of rebar, though, can be an issue at high temperatures that are below the threshold. I believe that differential temperatures with in the concrete contribute to this - for instance where the surface temperature rises fairly quickly and the internal core of the concrete stays cool. I don't think that's as much of an issue when temperatures rise more slowly and the entire mass of concrete can slowly ramp up to the high temperature at a uniform rate
- Concrete foundations in high-temperature uses can also be damaged by thermal expansion and contraction of the equipment it supports. The equipment is typically made of steel or some other metal and expansion can be quite rapid. The thermal rise and expansion of the equipment can be much greater than that of the foundation, particularly if the foundation is a large mat in contact with the ground (a heat sink or cooling source). That differential expansion can lead to high stresses on anchor bolts or on individual piers supporting the equipment - particularly those at the far ends of the equipment. For this situation you can see if the equipment manufacturer can allow slotted holes and slide bearings in the baseplates to allow for expansion and contraction relative to the foundation. In lieu of that, make sure any anchor bolts have adequate edge distance and preferably also some confining reinforcing bars. If the foundation will be restraining expansion consider extra reinforcing to accommodate the additional loads due to thermal expansion being restrained.
Honestly (thinking about it now) 70C isn't really that high (158 F) compared to some of the exposures we'd see in steel mills. I wouldn't be too concerned about it - pavement can get up to 130 to 140 F on a very hot sunny.
Greg Thein
Greg Thein, PE
Cleveland, OH