I've done heavy civil construction and have run across this situation upon occasion. I don't know if you took concrete cylinders, but a 7 day break should be at 80% capacity if you are to determine you are on track to achieve concrete strength. It is possible to determine the yield capacity of your L lags as the diameter of the bold and steel grade. This is the capacity you want in your epoxy substitute. We calculated a conic pull-out capacity of our concrete to determine required bolt depth at 125% capacity (ignore stirrups). Lag embedment is variable with changing conic surface area so setting up the equation for capacity will yield depth. We then chose a low creep epoxy to sustain that load. As an added tip, the contractor *Must* blow out the holes thoroughly before applying epoxy. That little bit of drill dust can dramatically reduce pull out capacity. In the end, if a pull-out test is conducted (on a set-aside test bolt), you should find you have reliable full capacity for your design.
Matt
------------------------------
Matthew Socha P.E., M.ASCE
Transportation Engineer
Eureka CA
------------------------------