Dear Mr. Rodriguez,
I believe checking crack width would be part of Serviceability Limit State (stress limitation, aesthetics, drainage, deflection, creep, vibrations, reinforcement corrosion, watertightness) using load factors of 1.0 unless you are conducting a special limit state analsyis. The reinforcement tensile stress limitation rules at SLS in ACI 318 (e.g limiting f
s to 2/3 of f
y) along with minimum reinforcement ratio and maximum reinforcement spacing rules are intended to limit crack widths without having to calculate them directly.
See
ASCE 7-10 Commentary Appendix C - Serviceability Considerations for load combinations (mostly for static loads) used to check SLS. Load combinations may include wind to check drift but I can't think of a situation where they would include seismic loads (maybe for critical tank structures??).
Hope this is helpful :)
------------------------------
Robert Yates P.E., M.ASCE
Senior Civil Engineer
ROY Structural and Materials Engineering
Roseville, CA
------------------------------