  • 1.  Cantilevered column system: concrete columns connecting wood-framed building to deep foundation

    Posted 8 days ago
      |   view attached

    We are designing a beach house; the complication lies in justifying the lateral force resisting system and transfer to foundation at a difficult coastal location. The essence of the question is this: the SFRS selection from ASCE 7-16 Table 12.2-1 and site and building criteria allow us only one option: "Cantilevered column systems detailed to conform to the requirements for special reinforced concrete moment frames". The problem is that this system, by way of ACI detailing, implies beams. However, the columns terminate at the soil level and soil grade beams have proven to be very costly. Can the cantilever system, without the use of any grade beams, utilize the soil restraint around discrete footings/pile caps and tie directly to steel piles for bearing and moment fixity? I am aware of other projects that used discrete pile caps (one cap per pile and column) but I do not have confidence that ASCE-7 allows it. This is for Seismic SDC E; the question is not derived from wind design criteria although that is part of the design.

    Sketches are attached that convey more information. We have already designed Option 1 and as a value-engineering service are evaluating Option 2.



    ------------------------------
    Edward Tornberg M.ASCE
    Creative Building Works, LLC
    Medford OR
    ------------------------------

    Attachment(s)



  • 2.  RE: Cantilevered column system: concrete columns connecting wood-framed building to deep foundation

    Posted 6 days ago

    Ed

    The intent of the requirement to detail as per "special reinforced concrete moment frames" is to assure that appropriate confinement through ties and cross ties, and reinforcement splices (if any) are provided.  It is not intended to force you to construct grade beams.  One concern I might have about not providing grade beams is that the base of the columns will be quite flexible meaning that you may get substantial deflection of the top of the columns under load.  Grade beams would be an effective (if costly) way to minimize this effect, as would a beam at the top of the columns, in which case the substrucutre could be designed as an SMF or IMF with appropriate R factors.



    ------------------------------
    Ronald Hamburger, SE
    Consulting Principal
    Simpson Gumpertz & Heger
    ------------------------------



  • 3.  RE: Cantilevered column system: concrete columns connecting wood-framed building to deep foundation

    Posted 5 days ago
    Following up on Mr Hamburger's remarks, if there is a substantial diaphragm at the top of the columns, it would probably be reasonable to distribute the lateral forces on the basis of a rigid diaphragm. 

    On Mon, Jan 5, 2026 at 10:15 AM Ronald Hamburger via ASCE Collaborate <Mail@...> wrote:
    Ed The intent of the requirement to detail as per "special reinforced concrete moment frames" is to assure that appropriate confinement through...
    American Society of Civil Engineers

    Integrated Buildings & Structures

    Post New Message
    Re: Cantilevered column system: concrete columns connecting wood-framed building to deep foundation
    Reply to Group Online Reply to Group
    Jan 5, 2026 10:15 AM
    Ronald Hamburger

    Ed

    The intent of the requirement to detail as per "special reinforced concrete moment frames" is to assure that appropriate confinement through ties and cross ties, and reinforcement splices (if any) are provided.  It is not intended to force you to construct grade beams.  One concern I might have about not providing grade beams is that the base of the columns will be quite flexible meaning that you may get substantial deflection of the top of the columns under load.  Grade beams would be an effective (if costly) way to minimize this effect, as would a beam at the top of the columns, in which case the substrucutre could be designed as an SMF or IMF with appropriate R factors.



    ------------------------------
    Ronald Hamburger, SE
    Consulting Principal
    Simpson Gumpertz & Heger
    ------------------------------
      Reply to Group Online   View Thread   Like  




     
    You are subscribed to "Integrated Buildings & Structures" as pmpe31751@.... Reduce the amount of emails you receive by subscribing to a consolidated digest. Your consolidated subscriptions will arrive in one ASCE Collaborate email. Change here. To unsubscribe from this community discussion, go to Unsubscribe.



    Original Message:
    Sent: 1/4/2026 2:50:00 PM
    From: Ronald Hamburger
    Subject: RE: Cantilevered column system: concrete columns connecting wood-framed building to deep foundation

    Ed

    The intent of the requirement to detail as per "special reinforced concrete moment frames" is to assure that appropriate confinement through ties and cross ties, and reinforcement splices (if any) are provided.  It is not intended to force you to construct grade beams.  One concern I might have about not providing grade beams is that the base of the columns will be quite flexible meaning that you may get substantial deflection of the top of the columns under load.  Grade beams would be an effective (if costly) way to minimize this effect, as would a beam at the top of the columns, in which case the substrucutre could be designed as an SMF or IMF with appropriate R factors.



    ------------------------------
    Ronald Hamburger, SE
    Consulting Principal
    Simpson Gumpertz & Heger
    ------------------------------


  • 4.  RE: Cantilevered column system: concrete columns connecting wood-framed building to deep foundation

    Posted 5 days ago

    Ron,

    Thanks for that seasoned response and I agree that considering deflection is a greater issue to contend with than with grade beams. However, as the columns will be detailed for fixity with the piles (continuous curve through 10 to 20 feet of soft soil to bedrock) we should be able to create a reasonable model that estimates the deflection, adjusting pile cap/footing size as needed.  We do not have liquefaction potential but just soft near-surface soil to contend with, which contains organic material. The conventional MRF option was ruled out for reasons that would take too much space here to elaborate on but I appreciate that thought as well.   Your main point regarding the intent of the ASCE 7 SFRS description is sincerely appreciated.



    ------------------------------
    Edward Tornberg M.ASCE
    Creative Building Works, LLC
    Medford OR
    ------------------------------