Hello, Gary. I think it would be job dependent. If you're looking at a flexible wood foundation (historic restoration, perhaps), then absolutely. If you're looking at typical, continuous concrete footings I don't think it would as important. Consider this article from Structure Magazine:
Design of Shelf Angles for Masonry Veneer. Masonry veneer, while not something we often consider, has strength and stiffness (especially if joint reinforcing is provided). If you can design the masonry veneer as a "beam" to span an opening, the lintel and its L/600 limit becomes a constructability item more than anything so you don't have to shore all of the openings (unless the lintel is bolted to a wood header - then it's a different story again). When you apply this principle to the foundation, you should consider the short term deflections of the foundation. If they are severe enough that it would be a concern, you're probably on piles and your grade beam isn't going to deflect under the weight of a story or two of brick. (NOTE: I'm NOT advocating not using lintels - I'm just using this to illustrate a concept as it is a valid application of engineering mechanics and analysis.)
In short, I don't think it should be a matter of concern for a properly designed foundation. That doesn't mean you shouldn't use judgement, of course, where you end up with an abnormally high load in a pile that could produce some differential deflections and movements (or similar cases).
------------------------------
Peter Hamilton EIT, A.M.ASCE
Project Structural Engineer
------------------------------